TSPP from S7-1500

Post by tmalone »

Trying to get the S7 Driver in 3.14 P003 to talk TSPP with an S7-1500.

The biggest issue is that the documentation is still showing panels from Step7, which is not how you configure the latest S7-1200 or S7-1500 PLCs.

Our testing has found that the PCid from the S7 driver configuration allows values in hex to FF (255). But, in the TIA Portal, this setting starts at 100hex. The example is 02 in the manual, and it is clear that this is no longer a valid setting for the latest PLCs.

I tried using PARA to change the internal datapoints for this setting, but without any success.

Has anyone been able to use TSPP with S7-1500?

Todd Malone
Siemens USA

tmalone
Posts:192
Joined: Mon Nov 22, 2010 11:21 pm

Re: TSPP from S7-1500

Post by tmalone »

It seems that the ETM staff did have the information.

Here is what I received from them on this topic. https://www.winccoa.com/fileadmin/image ... Pmagic.zip
Attachments
TSPPmagic.zip
(332.62 KiB) Downloaded 206 times

Gertjan van Schijndel
Posts:634
Joined: Mon Aug 02, 2010 10:37 am

Re: TSPP from S7-1500

Post by Gertjan van Schijndel »

Did you get it working with the new information?

tmalone
Posts:192
Joined: Mon Nov 22, 2010 11:21 pm

Re: TSPP from S7-1500

Post by tmalone »

Yes. The OA docs could use some updates in this topic.