No re-connect to the redundant servers from a remote UI after loss of communication with both servers.

Discussions about product bugs & problems!
Note: This is no replacement for the Official ETM Support!
2 posts • Page 1 of 1
akim
Posts:42
Joined: Wed Sep 16, 2015 10:48 am

No re-connect to the redundant servers from a remote UI after loss of communication with both servers.

Post by akim »

Hello,

A message box appears after loss connection with the both redundant servers:

Image

I click on "Try to continue".

After that Vision module remains but there is no re-connection to the Event Manager.
Requires restart of UI manager on a remote UI.

How can I solve this problem?

My configs

[general]
pvss_path = "C:/Siemens/Automation/WinCC_OA/3.12"
proj_path = "D:/WinCCproj/ARM1"
proj_version = "3.12"
data = "ezbar1$ezbar2"
event = "ezbar1$ezbar2"
userName = "root"
password = ""
langs = "en_US.utf8"
langs = "ru_RU.utf8"

[ui]
loadCtrlLibs = "bars_lib.ctl"
checkChildPanelPos = 2
childSystemMenu = 0
showQuitDialog = 1

[other]
proj_path = "\\\\192.168.0.5\\wincc_proj\\ezbar_v1"
Attachments
mes.jpg

mkoller
Posts:741
Joined: Fri Sep 17, 2010 9:03 am

Re: No re-connect to the redundant servers from a remote UI after loss of communication with both servers.

Post by mkoller »

In all versions < 3.14 there is no auto-reconnect feature.
You can use pmon to start and restart the UI and set the showQuitDialog option to 0

2 posts • Page 1 of 1