Change userbits from PLC

Find and share HowTos to various installations / configurations!
2 posts • Page 1 of 1
twinsen
Posts:16
Joined: Mon Jan 30, 2017 1:31 pm

Change userbits from PLC

Post by twinsen »

Is there a way to set a datapoint element's userbits from PLC?
I have a dpe read from a SIMATIC PLC, I want the dpe's userbits to be set/reset by that plc too.

Gertjan van Schijndel
Posts:634
Joined: Mon Aug 02, 2010 10:37 am

Re: Change userbits from PLC

Post by Gertjan van Schijndel »

There is no standard way to set userbits from a PLC. Drivers are designed to read/write values, depending on the protocol the value has additional (status/quality) information which could be mapped to userbits.
For example the following drivers can map information to the userbits: SINAUT, OPC (UA), IEC104, DNP3 & BACnet.

With a simatic plc it is also possible to use the open user communication for (UDP) communication with a control script, which could set the userbits.

2 posts • Page 1 of 1